Have a great invention to help with gardening? Are you the self-reliant type that prefers Building It Yourself vs. buying it? Share and discuss your ideas and projects with other members.
|
|
Thread Tools | Display Modes |
June 15, 2017 | #166 |
Tomatovillian™
Join Date: Jun 2012
Location: Illinois, zone 6
Posts: 8,407
|
Thanks, Worth. I forgot about this thread.
For anyone else's benefit, the question was that I just bought an air conditioner rated at 14 amps, plugged it into a 15 amp circuit with nothing else on the circuit, and it keeps flipping the breaker. The unit was on clearance because it had been discontinued...now maybe I have found the reason for that happening. |
June 15, 2017 | #167 | |
Tomatovillian™
Join Date: Jan 2015
Location: Columbus, MS Living on the Edge ( Of Zone 7b/8a that is..)
Posts: 50
|
Quote:
So that said - A 14 amp air conditioner really needs a 20 amp circuit to operate with out issues. That would be #12 wire and a 20 amp breaker. If your wiring is already #12 then just change the circuit breaker to 20 amps. If the wiring is #14 - you really need to run a separate #12 wire circuit to the unit on a 20 amp breaker. I enjoy reading all your gardening posts and learn from them - I hopes this helps you. Frank |
|
June 15, 2017 | #168 |
Tomatovillian™
Join Date: Jun 2012
Location: Illinois, zone 6
Posts: 8,407
|
Thanks, Frank. That does help.
|
June 15, 2017 | #169 |
Tomatovillian™
Join Date: Apr 2016
Location: Dallas, TX
Posts: 3,825
|
While you're at it, you might want to invest in a 20A fixture (outlet). They cost more - $3-4 - but are much more robust that the 99¢ contractor specials that never expect to see 15A. If it were me, I'd use a single rather than duplex outlet just so I wasn't tempted to plug anything else into it.
__________________
Stupidity got us into this mess. Why can't it get us out? - Will Rogers |
June 15, 2017 | #170 |
Tomatovillian™
Join Date: Jun 2012
Location: Illinois, zone 6
Posts: 8,407
|
I agree. I always buy the heavy-duty outlets, anyway. It is worth the extra money.
|
June 15, 2017 | #171 |
Tomatovillian™
Join Date: Feb 2006
Location: Den of Drunken Fools
Posts: 38,539
|
Someone remind me please to get a 240 male three prong drier plug this weekend and a bag of Ironite.
I keep forgetting. Worth. |
June 16, 2017 | #172 |
Tomatovillian™
Join Date: Feb 2006
Location: Den of Drunken Fools
Posts: 38,539
|
I'm sure in the manual of Coles AC it says connect to 20 amp circuit.
I highly doubt that my garage/shop is using anything close to 50% more like 40% or less capacity. Most of the time zero. |
June 16, 2017 | #173 |
Tomatovillian™
Join Date: Apr 2016
Location: Dallas, TX
Posts: 3,825
|
Hey Worth, don't forget the dryer plug and ironite.
I hope that the two are not part of the same project.
__________________
Stupidity got us into this mess. Why can't it get us out? - Will Rogers |
June 17, 2017 | #174 |
Tomatovillian™
Join Date: Jun 2012
Location: Illinois, zone 6
Posts: 8,407
|
So here's another question, I took the cover off the panel to look at it for wiring the new circuit. Every once in a while, the panel made a noise. It wasn't too loud, but it sounded like a bug zapper, jedi light saber, tesla coil type of noise. I turned everything off on the circuit, and eventually deduced that it was making that noise when a window unit AC was kicking on. The AC is very small, 6,000 btu, and does not use anywhere near 15 amps. The breaker has never tripped.
Is Jedi Light Saber noise bad? Should I replace the breaker? |
June 17, 2017 | #175 |
Tomatovillian™
Join Date: Feb 2006
Location: Den of Drunken Fools
Posts: 38,539
|
Sounds like a loose connection.
|
June 17, 2017 | #176 |
Tomatovillian™
Join Date: Apr 2016
Location: Dallas, TX
Posts: 3,825
|
Yeah. An arc like that will degrade the connection, to no good effect. Best case, contact will no longer be made.
If you feel comfortable doing it, try tightening the screw on the neutral (white) connection and unsnapping and re-inserting the breaker. (Assuming you have snap-in breakers.) So is there 12GA on the big A/C circuit?
__________________
Stupidity got us into this mess. Why can't it get us out? - Will Rogers |
June 17, 2017 | #177 |
Tomatovillian™
Join Date: Jun 2012
Location: Illinois, zone 6
Posts: 8,407
|
There's no 12 gauge wire installed now. They only put four rooms on one circuit, 12 ga would obviously be overkill, right?
I did buy 12 gauge for the new 20 amp circuit, though. |
June 17, 2017 | #178 |
Tomatovillian™
Join Date: Apr 2016
Location: Dallas, TX
Posts: 3,825
|
Many electricians wire a whole house in 12Ga just so they don't have to deal in two different wire sizes. Easier and less possibility of error. 12Ga is more expensive but not that much.
__________________
Stupidity got us into this mess. Why can't it get us out? - Will Rogers |
June 17, 2017 | #179 |
Tomatovillian™
Join Date: Feb 2006
Location: Den of Drunken Fools
Posts: 38,539
|
I think they should ban 14 AWG wire for home wiring.
As for the buzz it could be coming from the connection side of the breaker too. This would be the side that runs to you outlets and so on. You can turn the breaker off, this will make the terminal connection dead. Check it too but be careful. Then it could be the breaker itself. |
June 17, 2017 | #180 | |
Tomatovillian™
Join Date: Jan 2015
Location: Columbus, MS Living on the Edge ( Of Zone 7b/8a that is..)
Posts: 50
|
Quote:
Of course switch the load breakers to off before doing this or if not comfortable putting a screw driver in an electrical panel board - open the main circuit breaker first - that is the safest way. My answers are to long...sorry. Frank |
|
Thread Tools | |
Display Modes | |
|
|